[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: (ET) rotary inverter specifics
Couldn't one use a line conditioner off the rotary inverter to correct for
voltage variances?
(---------------------------)
mailto:Jeremy Gagliardi com
http://Jeremy.Gagliardi.com
(---------------------------)
----- Original Message -----
From: "The Nauglers" <snaugler earthlink net>
Date: Sun, 3 Oct 2004 14:20:51 -0400
To: "elec-trak" <elec-trak cosmos phy tufts edu>
Subject: Re: (ET) rotary inverter specifics
> Thon,
>
> The rotary inverter will have a sine wave output. The only reason an
> induction motor may not like the rotary inverter would be how good the
> voltage regulation was. This includes both continuous voltage output
> stability and the capability to handle inrush, or starting, currents and
> the
> voltage drop that occurs when that inrush to your load happens.
>
> It is possible that a rotary inverter may not handle the starting
> current of
> your induction motor. If the inrush capability is too low the output
> voltage will drop, and sometimes the inverter will slow down and the
> frequency will also drop. In either case that is bad for both the
> inverter
> and the motor you are trying to run, and frequently you can't even get
> the
> motor to start.
>
> While more often a flaw in the ratings of electronic inverters, you need
> to
> make sure that your rotary inverter has the following two specifications:
> 1. A continuous current output that meets or exceeds the continuous
> draw of
> your inductive (motor) load.
> 2. A surge, inrush, starting, or peak current rating that is at least
> three
> to five times the running current of your inductive load. It only has to
> maintain this higher current for two to five seconds, as long as it takes
> the inductive load to reach normal operating conditions.
>
> This rating applies to generators too. I had a friend whose well pump
> would
> not start when run off a Coleman 4000 watt generator. That same well
> would
> start and run off a Honda 3500 watt generator. The lower watt rated
> Honda
> had a higher ability to handle the well's inrush starting current.
>
> There are some military rotary inverters out there with a 400 Hz output,
> so
> beware of them. A load designed for 60 Hz operation will not run off of
> them, but many unversal motors will.
>
> Steve Naugler
> snaugler earthlink net
>
> ----- Original Message -----
>
>
> > Could someone explain why a 2250W rotary inverter would not "operate
> > induction type motors found in fans, furnace blowers, washers,
> > dryers,etc
> ".
> >
> > Thanks.
> > Thon
>
>
>
> _______________________________________________
> Elec-trak mailing list
> Elec-trak cosmos phy tufts edu
> https://cosmos.phy.tufts.edu/mailman/listinfo/elec-trak